Is there any way to adjust the charging amperage?




Last edited by GreasedFolgore; Jul 19, 2024 at 09:22 AM.
The Chargepoint charger should not allow you to adjust the charging current above the allowed limit for the circuit. Usually, the allowed current will be set by the equipment installer to match the rated continuous load capacity of the circuit. The car will draw as much as it needs up to the limit, and may draw less depending on the battery state (i.e., charge level, temperature, etc.).
Trending Topics

The max AC charging power for us in Europe is 11 kW or 22 kW, option dependent.
The Best of Mercedes & AMG
In the US most houses are supplied single phase 240 AC power, with both 240V and 120V circuits available.
120V/15A circuits are the most common, and allow a max charging current of 12A (to meet 80% continuous load limitations) or 1.44 kW.
120V/20A circuits are less common, but allow 16A or 1.92kW charging
240V circuits are usually 30A or 50A supporting Dyers, Ovens, and Air Conditioners. These would support 24A and 40A or 5.76kW and 9.6kW charging. However, J1772 standard allows charging currents as high as 80A , which would allow 19.2kW charging if the AC inverter in the car supported it.
Note that the above applies to both CCS1 and NACS (which uses the same control protocol) for AC charging.
In Europe, 240C three phase service is available to houses, which means three phase 240V or single phase 208V charging is available.
It appears the most common charging circuits are 16A or 32A at the voltages above. The standard allows up to 80A single phase and 63A three phase charging.

The Chargepoint charger should not allow you to adjust the charging current above the allowed limit for the circuit. Usually, the allowed current will be set by the equipment installer to match the rated continuous load capacity of the circuit. The car will draw as much as it needs up to the limit, and may draw less depending on the battery state (i.e., charge level, temperature, etc.).