IC heat exchanger
larger (more efficient) heat exchangers, higher pump flowrates and positioning of the heat exchangers will make the best effect on the system. once you add these auxillary systems that require additional maintenance, you take away its driveability and reliability. i wouldn't want to be driving everyday wondering if i'm getting leakage of CO2 into my intake.
ultimately, you'll also need to check how much heat these installed components reject (in terms of kW or BTU/min) for your particular configuration. Manufacture claimed temperature changes are totally dependant on both the inlet temperatures and mass flows of both mediums involved. Of course something could lower intake temps 10 degrees, but you could be slowing down the flowrate enough to reach those temps...
Although I appreciate your trial and error experimenting on these new parts, you may be able to save your time (and money) if you figure out how well the components actually reject heat and the resulting pressure drops they induce.
Larger Front Mounted Coolers typically are a given, since increasing the amount of passes can possibly decrease pressure drop (resulting in more flow from the pump) while increasing the effective heat transfer area. The air inlet mass flow (cooling medium) is high also, since it's in front of the CRFM getting the most of ram air. Look at the ports in those components you plan to install. How much flowrate are you getting? Although the inlet temps might be low, I doubt you're getting enough mass flow to make it effective.......
regarding the whole "frost on the intake", curious at what conditions will you see this.....
Put that in-line in the liquid cooling circuit and you should see something !!!
for a given heat exchanger, if the I.T.D (Inlet temperature differential) is greater, you get more heat rejection. Putting the cooler in an area of flow which temperatures are closer to ambient, you get less heat rejection (lower decrease in inlet temperature), opposed to putting the cooler post heat source where inlet temperatures are much greater.
so in effect, if you put it "pre-charger", the heat source does not erase the gains. the gains "pre-charger" are simply less than post-charger
for a given "cooler", you want to put it where the temps it's trying to cool are the greatest.
I want to upgrade my water cooling system this way; I already have a CM90, just need to find an appropriate HE from afco.
I can help you out with the HE. I bought a AFCO pro series dual pass HE (made for modded cobras) and just had the inlet/outlet relocated to the side by cutting them off and rewelding them. The HE is MASSIVE so make sure you have clearance on your car before upgrading. Hope that helps.
a possible improvement is to spray the heat exchanger with some form of water/cooling medium to increase the specific heat capacity. Water vapor transfers heat much better than dry air alone.
Lets check math -
Q = m*Cp*(T2 - T1)
where
Q = Heat Transfer (kW)
m = mass flow of cooling air medium (assume .5 kg/s)
Cp = specific heat of cooling air medium (1.01 kj/kg_C)
T2 = Temperature of Cooling air medium (assume 25C for ambient air)
T1 = Temperature of Coolant (assume 100C for coolant)
So for normal cooling conditions, you get the following:
Q = .5 * 1.01 * (25 - 100) = -37.9 kW heat rejected to air
Senario 1 - Making the cooling air 10C cooler
Q = .5 * 1.01 * (15 - 100) = -42.93 kW heat rejected to air
Scenario 2 - Making the cooling air into water vapor (via some form of water spray)
The Cp of water vapor is 1.86. Of course this is with 100% saturation of water in the air. Air droplets would increase this number, while an incomplete saturation would decrease.
Q = .5 * 1.86 * (25 - 100) = -69.75 kW heat rejected to water vapor
Increasing the Cp to 1.15 would make it comparable to lowering ambient temps 15C. I don't know the exact Cp value of adding a sprayer, and I didn't account for density changes by adding water to the air, but you get the effect.
Sorry for rambling
This is why some makers utilize water sprayers for heat exchangers... however it's added complexity adding a completely different system.
I'm intending to try to fit upgraded '04 cobra he- but haven't really looked at how much cutting i want to do yet either
-drew