Originally Posted by SW20S
Agreed, don't unplug and replug...
Do you mind explaining why you agree?
Old 06-04-2024, 08:25 PM
  #77  
MBWorld Fanatic!
 
SW20S's Avatar
 
Join Date: Jun 2015
Location: Maryland
Posts: 5,189
Received 2,556 Likes on 1,653 Posts
2020 S560 4Matic
Originally Posted by MB2timer
Do you mind explaining why you agree?
The outlets are not designed for that many plug/unplug cycles...it wears the outlet out. As was said above the rated life of the outlet is about 350 plug/unplug cycles. They just dont anticipate people plugging and unplugging 220v outlets all the time.
Old 06-04-2024, 09:15 PM
  #78  
MBWorld Fanatic!
 
AppleFan1's Avatar
 
Join Date: Feb 2014
Location: Iowa
Posts: 1,766
Received 298 Likes on 207 Posts
2022 EQS580
Originally Posted by SW20S
The outlets are not designed for that many plug/unplug cycles...it wears the outlet out. As was said above the rated life of the outlet is about 350 plug/unplug cycles. They just dont anticipate people plugging and unplugging 220v outlets all the time.
I think I plugged and unplugged maybe 25 times in two+ years. I almost always use EA. BUT since the free charging is ending if it hasn’t already, I’ll be using the ChargePoint wall charger more frequently. For long trips, I’ll charge it to 100%.
Great info from this forum.
Old 06-04-2024, 10:23 PM
  #79  
MBWorld Fanatic!
 
SW20S's Avatar
 
Join Date: Jun 2015
Location: Maryland
Posts: 5,189
Received 2,556 Likes on 1,653 Posts
2020 S560 4Matic
Originally Posted by AppleFan1
I think I plugged and unplugged maybe 25 times in two+ years. I almost always use EA. BUT since the free charging is ending if it hasn’t already, I’ll be using the ChargePoint wall charger more frequently. For long trips, I’ll charge it to 100%.
Great info from this forum.
Still just not a good idea. Those outlets are designed to have something plugged in and just left there. The charger is basically just like a cord when its not plugged into the car, perfectly safe to leave it plugged in.
The following users liked this post:
AppleFan1 (06-04-2024)
Old 06-05-2024, 12:58 AM
  #80  
MBWorld Fanatic!
 
Diesel Benz's Avatar
 
Join Date: Dec 2006
Location: Europe
Posts: 6,364
Received 294 Likes on 246 Posts
223.168 & 213.012 & 906.633 & 214.005
Originally Posted by AppleFan1
I think I plugged and unplugged maybe 25 times in two+ years.
...
I have the European style 3 phase 11 kW charger with a plug. Although only 16 A, I just unplugged and plugged it again after reading this thread. I thought it would be healthy for the contact surfaces to rub out any corrosion or what ever they may have. Never seen any hard facts which way would be better. I understand the max cycles for any plug and some may have a significantly lower max figure but surely these would not exist if they were supposed to be used only once! 25 times in 2 years is more or less "only once"?
Old 06-05-2024, 05:49 AM
  #81  
MBWorld Fanatic!
 
Crito's Avatar
 
Join Date: Apr 2023
Location: Occupied Palestine
Posts: 1,000
Received 374 Likes on 253 Posts
2023 EQE 500 SUV electric and 2024 Jaguar F-PACE SVR 5.0L
Just bought a brand new house and one of the electrical outlets is so loose my surge suppressor literally fell out on its own. Duty cycle is apparently one plug-in.
The following users liked this post:
Diesel Benz (06-06-2024)
Old 06-05-2024, 09:48 AM
  #82  
MBWorld Fanatic!
 
SW20S's Avatar
 
Join Date: Jun 2015
Location: Maryland
Posts: 5,189
Received 2,556 Likes on 1,653 Posts
2020 S560 4Matic
Originally Posted by Diesel Benz
I have the European style 3 phase 11 kW charger with a plug. Although only 16 A, I just unplugged and plugged it again after reading this thread. I thought it would be healthy for the contact surfaces to rub out any corrosion or what ever they may have. Never seen any hard facts which way would be better. I understand the max cycles for any plug and some may have a significantly lower max figure but surely these would not exist if they were supposed to be used only once! 25 times in 2 years is more or less "only once"?
Nobody is saying that 25 plugs and unplugs will ruin the outlet, but the point is that the outlet is not designed for you to plug and unplug it a bunch of times like a 110v outlet. So if your goal is to increase safety, you increase safety by using the plug the way it was intended, which is to have things plugged in long term and not plugged and unplugged. Best case unplugging it when not in use does nothing, worse case it increases fire risk. Just smart not to do that.
Old 06-05-2024, 10:36 AM
  #83  
Senior Member
 
MB37's Avatar
 
Join Date: Apr 2011
Posts: 460
Received 146 Likes on 94 Posts
23'EQS AMG
Arcing is the the most likihood of melting and fire at receptacle plugs. If you have a loose receptale/plug, replace it. Make sure that the wires are torqued properly according to code. It doesn't matter how many times you unplug/plug in X number of months or years. Industrial grade or WR (water resistant) receptacles will always be more durable than your standard household ones. The reason hardwire is recommended is because it removes the unpluggable connection which presents potential electrical arcing over time.

Now, if you have leviton or household grade receptacle, the outlet/plug is tight, and the wires are torqued to spec, I personally don't think you need to replace your recepable. However, for a peace of mind, replace it with an industrial grade receptable if you plan to plug/unplug frequently. Even at 9.7kw charging, a properly installed household 14-50 will reach temps of around 116-122 F which is in normal operating temperature. When you get to l50 F, you have a problem. Assuming you have at least a 50amp breaker, you can lower our EV charger down to 32A, and that will lower the heat resistance in your wire/connection when charging. But remember, a loose connection is a problem regardless, and electrical arcing is NOT your friend. Similarly, just because your car accelerate to 60mph in less than 5 seconds doesn't mean you need to do that all the time.
The following 2 users liked this post by MB37:
MBNUT1 (06-06-2024), SW20S (06-05-2024)
Old 06-05-2024, 10:53 AM
  #84  
Super Member
 
lkfoster's Avatar
 
Join Date: Aug 2007
Location: Phoenix AZ & Cayucos CA
Posts: 745
Received 42 Likes on 31 Posts
'19 AMG E53 Cpe, '23 EQS 580 SUV, '89 560SL, '35 Ford 5w coupe, '53 MGTD and others
I measured 108F at my 14-50 plug that had been charging at 9.7kW for several hours. Same surface temperature for the lead to the Charge point unit. This was at 95F in the garage.
Old 06-05-2024, 12:36 PM
  #85  
MBWorld Fanatic!
 
Crito's Avatar
 
Join Date: Apr 2023
Location: Occupied Palestine
Posts: 1,000
Received 374 Likes on 253 Posts
2023 EQE 500 SUV electric and 2024 Jaguar F-PACE SVR 5.0L
I guess now might be the time for a friendly reminder that it's the amps that'll kill ya.... but it's the volts that make spectacular arcs of plasma.

Old 06-05-2024, 01:57 PM
  #86  
Senior Member
 
nosnoop's Avatar
 
Join Date: Jul 2012
Posts: 376
Received 84 Likes on 58 Posts
535
Originally Posted by MB37
Now, if you have leviton or household grade receptacle, the outlet/plug is tight, and the wires are torqued to spec, I personally don't think you need to replace your recepable. However, for a peace of mind, replace it with an industrial grade receptable if you plan to plug/unplug frequently.
A Leviton consumer grade has a torque spec of 25 in-lbs while Hubbell has a torque spec of 75 in-lbs.
Have a look at this page for a more detailed comparison: https://teslamotorsclub.com/tmc/thre...-guide.140694/
IMHO, replace it if you have consumer grade.
Old 06-05-2024, 03:18 PM
  #87  
MBWorld Fanatic!
 
AppleFan1's Avatar
 
Join Date: Feb 2014
Location: Iowa
Posts: 1,766
Received 298 Likes on 207 Posts
2022 EQS580
Originally Posted by SW20S
Still just not a good idea. Those outlets are designed to have something plugged in and just left there. The charger is basically just like a cord when its not plugged into the car, perfectly safe to leave it plugged in.
Yes, I understand now. I will leave plugged in from now on.
The following users liked this post:
SW20S (06-05-2024)
Old 06-06-2024, 06:23 PM
  #88  
Junior Member
 
Sparky66's Avatar
 
Join Date: Jan 2023
Posts: 56
Received 18 Likes on 15 Posts
V167
Not totally correct. The wire ampacity is rated based on the termination points. I have never seen a breaker or a receptacle rated @90c. Most are 40c. As such the lowest rated termination is the maximum allowable ampacity of the cable in the table. The point is to keep the heat down so that the insulation never degrades.
Old 06-12-2024, 03:51 PM
  #89  
Super Member
Thread Starter
 
hlothery's Avatar
 
Join Date: Jan 2022
Location: Texas
Posts: 827
Received 423 Likes on 271 Posts
EQS 450+
Just another word on this. I just received a $2500 check from the original installer to reimburse me for that improper install and cover my upcoming drywall repairs. I have a scheduled install of 6ga wire, directly wired to my ChargePoint Homeflex, which is currently charging my car at 32amps/7.7kW safely with the existing cable directly wired, until the new install. This new install will give me a safe circuit, capable of delivering 40amp/9.6kW of charging power without worry. Having experienced the garage fire, which was scary as heck, I would not recommend a NEMA plug installation for any home charger. Make sure you have a working 50 amp circuit, which means breaker and wire rated for that, directly wired to your charger. We thought we did, but it was not installed properly, and we didn't. Several folks have expressed reluctance to pay what it takes to do this right. My advice is, don't skimp on this. Do it right the first time, We almost lost our house. Do not make that mistake.
The following 4 users liked this post by hlothery:
dangitty (06-13-2024), MBNUT1 (06-12-2024), Surge (06-12-2024), SW20S (06-12-2024)
Old 06-12-2024, 04:08 PM
  #90  
MBWorld Fanatic!
 
c4004matic's Avatar
 
Join Date: Oct 2014
Location: WI
Posts: 4,343
Received 1,088 Likes on 718 Posts
17 E43; 21 GLS580
Glad that its working itself out. However there is no need to worry about a plugged install. The EQS 9.5 kw charger is amply safe with a correctly installed plug install. The big issue is the dearth of competent electricians. When I did my home install, I was under the impression that the car was going to have an 11.5 charger (it hadn't been cleared up yet) thus I has a 60 amp circuit enstalled. When I installed it in our other home I did a 50amp circuit. They both work flawlessly using a plug. The cables dont even get warm!
Old 06-12-2024, 04:59 PM
  #91  
MBWorld Fanatic!
 
Surge's Avatar
 
Join Date: Jun 2014
Location: New York, NY
Posts: 1,879
Received 411 Likes on 287 Posts
W463 G550 / C190 GTC //prev: W204 C63 507 / R170

The following 2 users liked this post by Surge:
hlothery (06-12-2024), MBNUT1 (06-12-2024)
Old 06-12-2024, 07:42 PM
  #92  
MBWorld Fanatic!
 
SW20S's Avatar
 
Join Date: Jun 2015
Location: Maryland
Posts: 5,189
Received 2,556 Likes on 1,653 Posts
2020 S560 4Matic
Originally Posted by hlothery
Just another word on this. I just received a $2500 check from the original installer to reimburse me for that improper install and cover my upcoming drywall repairs. I have a scheduled install of 6ga wire, directly wired to my ChargePoint Homeflex, which is currently charging my car at 32amps/7.7kW safely with the existing cable directly wired, until the new install. This new install will give me a safe circuit, capable of delivering 40amp/9.6kW of charging power without worry. Having experienced the garage fire, which was scary as heck, I would not recommend a NEMA plug installation for any home charger. Make sure you have a working 50 amp circuit, which means breaker and wire rated for that, directly wired to your charger. We thought we did, but it was not installed properly, and we didn't. Several folks have expressed reluctance to pay what it takes to do this right. My advice is, don't skimp on this. Do it right the first time, We almost lost our house. Do not make that mistake.
I'm glad they owned up for it and made it right the only way they could...
Old 06-12-2024, 08:06 PM
  #93  
Super Member
Thread Starter
 
hlothery's Avatar
 
Join Date: Jan 2022
Location: Texas
Posts: 827
Received 423 Likes on 271 Posts
EQS 450+
Originally Posted by SW20S
I'm glad they owned up for it and made it right the only way they could...
Surprising, but also glad. Can't change what they did, but at least I got my money back, plus some for repairs.
The following users liked this post:
SW20S (06-13-2024)
Old 06-12-2024, 09:54 PM
  #94  
MBWorld Fanatic!
 
Crito's Avatar
 
Join Date: Apr 2023
Location: Occupied Palestine
Posts: 1,000
Received 374 Likes on 253 Posts
2023 EQE 500 SUV electric and 2024 Jaguar F-PACE SVR 5.0L
Originally Posted by Crito
Was watching a YouTube video (cant find it again sorry) where a hardwired install caught fire...
I don't know why this guy's videos never show up when I search YouBoob but transgender vehicle news always seems to. :hmm: I guess he's too heterosexual for their algorithm.

The following 2 users liked this post by Crito:
hlothery (06-13-2024), MBNUT1 (06-12-2024)
Old 06-13-2024, 04:36 PM
  #95  
Super Member
Thread Starter
 
hlothery's Avatar
 
Join Date: Jan 2022
Location: Texas
Posts: 827
Received 423 Likes on 271 Posts
EQS 450+
Crito, that was a fantastic video, thank you so much. Wish I had seen it before my problem install. I will have mine done correctly and hard wired in about a week, can increase my ChargePoint charger's capacity back to 40 amps, and can feel safe. EVERYONE should watch this video and educate themselves about their installation. If you have a NEMA 6/50 or 14/50 plug that is not a Hubbel or similar high quality plug, you need to have it changed out before it melts down and your garage is on fire. Lesson's learned, for sure.

Last edited by hlothery; 06-13-2024 at 04:38 PM.
Old 06-13-2024, 08:49 PM
  #96  
MBWorld Fanatic!
 
c4004matic's Avatar
 
Join Date: Oct 2014
Location: WI
Posts: 4,343
Received 1,088 Likes on 718 Posts
17 E43; 21 GLS580
Originally Posted by hlothery
Crito, that was a fantastic video, thank you so much. Wish I had seen it before my problem install. I will have mine done correctly and hard wired in about a week, can increase my ChargePoint charger's capacity back to 40 amps, and can feel safe. EVERYONE should watch this video and educate themselves about their installation. If you have a NEMA 6/50 or 14/50 plug that is not a Hubbel or similar high quality plug, you need to have it changed out before it melts down and your garage is on fire. Lesson's learned, for sure.
State of Charge is on my favorites. Always excellent info.
Old 06-16-2024, 01:19 AM
  #97  
Super Member
 
lkfoster's Avatar
 
Join Date: Aug 2007
Location: Phoenix AZ & Cayucos CA
Posts: 745
Received 42 Likes on 31 Posts
'19 AMG E53 Cpe, '23 EQS 580 SUV, '89 560SL, '35 Ford 5w coupe, '53 MGTD and others
Originally Posted by lkfoster
I measured 108F at my 14-50 plug that had been charging at 9.7kW for several hours. Same surface temperature for the lead to the Charge point unit. This was at 95F in the garage.
Just checked again after charging for over than an hour at 40a/9.8kW and 100F ambient, 130F/54C at the lead closest to the plug. I understand that my Home Depot Leviton is only rated to 50C. I down-rated to 32A and will be replacing the receptacle with a Hubbell or Bryant.
The following 2 users liked this post by lkfoster:
hlothery (06-16-2024), MBNUT1 (06-16-2024)
Old 06-16-2024, 10:55 PM
  #98  
Senior Member
 
MB37's Avatar
 
Join Date: Apr 2011
Posts: 460
Received 146 Likes on 94 Posts
23'EQS AMG
Originally Posted by lkfoster
Just checked again after charging for over than an hour at 40a/9.8kW and 100F ambient, 130F/54C at the lead closest to the plug. I understand that my Home Depot Leviton is only rated to 50C. I down-rated to 32A and will be replacing the receptacle with a Hubbell or Bryant.
I assume you have at least a 50amp breaker and 6 AWG wiring. Amazon has the Hubbell for $50 and you will need the cover plate too which is around $8. The Leviton cover plate opening will be too small for Hubbell. Make sure to torque it to spec. I think it is around 71-75 in lb. The cable is a monster. I hope you have enough room in the box since the Hubbell connects to the back at a 90 degree whereas the Leviton comes straight in. Smart move to lower your charging to 32A/7.7kw. It should bring the temperature down to about 100-102F.
The following 3 users liked this post by MB37:
hlothery (06-17-2024), jcapotos (06-17-2024), MBNUT1 (06-17-2024)

Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 


You have already rated this thread Rating: Thread Rating: 0 votes,  average.

Quick Reply: Garage Charger Fire!



All times are GMT -4. The time now is 10:19 AM.